Class 2 seal offs?

kjroller

Senior Member
Location
Dawson Mn
Occupation
Master electrician
Can someone explain to me a situation where I would need a seal off fitting it a strictly class 2 div 1 area I see them all around my plant and it confuses me cause its not between enclosures as 502 states. Am I missing something? Specifically its on pipe 2 inches and larger in the area? Which i understand for a class 1 area but I dont see that rule in class 2.
 
Many do not understand the difference between the sealing rules for Class I and Class II. It is rare that you would need any seal fitting in a Class II installation.
 