Although not stated directly in the NEC, UL 1585 limits Class 2 transformers (and therefore Class 2 circuits) to 30 V RMS. 725.2 for a Class 2 Circuit states "...Due to its power limitations, a Class 2 circuit considers safety from a fire initiation standpoint and provides acceptable protection from electric shock ."
My question regards the choice of doorbell button equipment. Do doorbell buttons that will be located in wet locations need to be listed for wet locations? With the exception of some newer wireless buttons, I haven't found a wired button that states it is for wet locations. Is there such a thing? Isn't it possible (even at 30 V) that under the right conditions a significant shock could occur?
Take this into account. According to NIOSH literature, wet skin can have a resistance of only 1000 ohms and 30 milliamps is enough to cause a loss of muscular control. Therefore, a short in 30 V circuit in a wet location could result in a 30 mA current flowing through some unfortunate person's body.
I know this scenario is not probable...but as far as safety is concerned, I'm only interested in the possible.
My question regards the choice of doorbell button equipment. Do doorbell buttons that will be located in wet locations need to be listed for wet locations? With the exception of some newer wireless buttons, I haven't found a wired button that states it is for wet locations. Is there such a thing? Isn't it possible (even at 30 V) that under the right conditions a significant shock could occur?
Take this into account. According to NIOSH literature, wet skin can have a resistance of only 1000 ohms and 30 milliamps is enough to cause a loss of muscular control. Therefore, a short in 30 V circuit in a wet location could result in a 30 mA current flowing through some unfortunate person's body.
I know this scenario is not probable...but as far as safety is concerned, I'm only interested in the possible.