Class 3 div 1 or not.

Status
Not open for further replies.

Santiago

Member
I am doing an electrical design for a wood truss manufacturing building. The equipment in this building has a couple enclosed saws, one Metra-cut saw, and a few manual skill saws.
I have been told that the amount of fibers produced are far less than that of lets say a cabinet wood working plant.

Would this building still be considered a Class 3 division 1 area?
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Re: Class 3 div 1 or not.

This has been discussed in several threads:

http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=22;t=000021

http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=22;t=000025#000004

http://www.mikeholt.com/cgi-bin/codeforum/ultimatebb.cgi?ubb=get_topic;f=22;t=000053

My personal opinion is that, unless there is a significant continuous amount of air-born ?wood flour? present (not likely in most modern facilities), the location does not need to be classified.
 

john m. caloggero

Senior Member
Re: Class 3 div 1 or not.

RBAlex: I agree with you 100 percent.
If a dust layer greater than 1/8 in. thick is present under normal conditions, the area should be classified as Division 1. Dust is defined as:Any finely divided solid material 420 microns or less in diameter (i.e., material passing through a U.S. No. 40 Standard Sieve). Most of the material in the wood-working facility would be of a much larger size.
Good house keeping is required to keep debris from covering heat generating electrical equipment and acting as thermal insulation preventing dissipation of heat.
 

john m. caloggero

Senior Member
Re: Class 3 div 1 or not.

Extracted from NFPA 499.
Thickness of Dust Layer

Classification
Greater than 1/8 in. (3 mm):Division 1

Less than 1/8 in. (3 mm), but surface color not discernible: Division 2

Surface color discernible under the dust layer:
Unclassified
 