I'm looking for some guidance on a class 320 service installation that I am going to be doing at my personal (soon to be built) residence. For reference, I am a licensed master electrician in my home state, but I am not a contractor so I don't regularly do residential installations. Hopefully this question doesn't violate the forum rules, but if it does feel free to close it.
For the new residence that we're building this year, I'm looking at installing a 320 amp service that will serve two 200A load centers in the house. I've done an installation like this with a 320A Meter/Main combination unit on another residence previously, but am struggling to get metering equipment with the current supply chain issues that we're dealing with. I did manage to get a 320 A meter and separate 200A single breaker outdoor disconnects, and would like to mount them all together outside of the house.
My question comes down to proper grounding/bonding for this arrangement. With the Meter/Main combination unit, a single set of grounding electrodes were bonded to the neutral bus and enclosure. In this case, should I have a separate set of grounding electrodes for each of the disconnects (see Image 1 - attached)? Would one set of grounding electrodes suffice, and if so, do I bond the ground terminals between all three enclosures (see Image 2 - attached)?
For the new residence that we're building this year, I'm looking at installing a 320 amp service that will serve two 200A load centers in the house. I've done an installation like this with a 320A Meter/Main combination unit on another residence previously, but am struggling to get metering equipment with the current supply chain issues that we're dealing with. I did manage to get a 320 A meter and separate 200A single breaker outdoor disconnects, and would like to mount them all together outside of the house.
My question comes down to proper grounding/bonding for this arrangement. With the Meter/Main combination unit, a single set of grounding electrodes were bonded to the neutral bus and enclosure. In this case, should I have a separate set of grounding electrodes for each of the disconnects (see Image 1 - attached)? Would one set of grounding electrodes suffice, and if so, do I bond the ground terminals between all three enclosures (see Image 2 - attached)?