Class A FA wiring

Status
Not open for further replies.

mstrlucky74

Senior Member
Location
NJ
I thought the return loop was only for the the initiating devices and not the notification devices. Is this true? Thanks
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
I thought the return loop was only for the the initiating devices and not the notification devices. Is this true? Thanks

Initiating Device Circuits (IDC's) and Notification Appliance Circuits (NAC's) can both, either, or neither be wired as Class A for a given project. IF they are wired as Class A, they will have a return loop. Otherwise it ain't Class A.
 