I have a Garage with 80 x 80 flat ceiling. From the Bottom of Deck to 18 inches is Class B for Natural gas. I have no problems Here I can understand the 18 inches definition.

Problem is the Slope roof. Is it along the whole slope 18 inches. Or just 18 inches at the peak. I am install Trapeze at 24. Below peak. EMT where they will be below the 18 Inch Class B area.
 

Attachments

  • Explosion Proof Area under decking.png
    Explosion Proof Area under decking.png
    17.5 KB · Views: 10
  • Class 1 Div 2 Ceiling.png
    Class 1 Div 2 Ceiling.png
    31.2 KB · Views: 13
  • Explosion Proof Area under decking.png
    Explosion Proof Area under decking.png
    30.1 KB · Views: 12
To be honest, I have no idea what you mean about Class B in relationship to classifying your locations. Natural gas is Group D.

That said, the right-hand figure in your third diagram would be correct; i.e., the 18" would be measured from the peak. If properly ventilated, it may not need to be classified at all. See Table 511.3(D).
 
To be honest, I have no idea what you mean about Class B in relationship to classifying your locations. Natural gas is Group D.

That said, the right-hand figure in your third diagram would be correct; i.e., the 18" would be measured from the peak. If properly ventilated, it may not need to be classified at all. See Table 511.3(D).
Acuttally better said Class 1 Division 2 Class b was a term I learned in the early 90s Stuck with me
 