Trying to bone up on GFCI over and above the run of the mill Class A type. The article I'm reading says that Class C is "for use in circuits with no conductor more than 300 V to ground (i.e.,
systems where line-to-line voltage is 480 V or less) where reliable equipment grounding or double insulation is provided."
OK - so for practical purposes, this targets 480Y/277V circuits, but here are my questions:
GFCI is different from the ground fault we are required to provide on 1000A and above feeders correct. Are circuit breakers available with Class C GFCI or do you have to provide separate protection. Where would that typically be located? I'm guessing it comes with the equipment and that it's mostly an OEM concern. True?
systems where line-to-line voltage is 480 V or less) where reliable equipment grounding or double insulation is provided."
OK - so for practical purposes, this targets 480Y/277V circuits, but here are my questions:
GFCI is different from the ground fault we are required to provide on 1000A and above feeders correct. Are circuit breakers available with Class C GFCI or do you have to provide separate protection. Where would that typically be located? I'm guessing it comes with the equipment and that it's mostly an OEM concern. True?