Can't dau that ive looked at it this closely yet. Do they specify class j (typically) or just 'current limiting'.
We're a distributor for the components too, so the price differences aren't quite as drastic at least. (Between class Cc vs J anyways)
Most contactors, VFDs, overloads, etc. that I've seen will require a specific class of fuse, and they will also specify the maximum size of said fuse in order to achieve the high SCCR. This is completely manufacturer dependent because it has to do with how the manufacturer tested and listed the component.
Looks like AB (for example) says you can use either J or CC fuses for their small IEC contactors to get 100kA, but I've seen other manufacturers that will only list one or the other. And technically J and CC fuses have different current limiting characteristics, so as far as SCCR is concerned they aren't interchangeable without doing some calculations.
On that note, UL 508A supplement SB has an exception where if a "High SCCR" for a component is achieved by a specific class of fuse, you are allowed to swap it for another class of fuse AS LONG AS the peak let-through and I
2t are NOT GREATER than the specified fuse. Note that to do this, you must use the umbrella fuse values for I
p and I
2t that UL has; you aren't allowed to use the fuse manufacturer's data sheet for this.
If you need to do that, I highly suggest you read up on it to make sure it suits your application because there are some other details that you need to be aware of. In practice I don't find that this is very useful, but I haven't had a situation where I can't use what the manufacturer specifies. Usually it's more trouble than it's worth.