Can someone please verify my statements here.
According to 2023 edition of NFPA 70 NEC 500.8.B.1 "Equipment shall be identified not only for the class of location but also for the explosive, combustible, or ignitible properties of the specific gas, vapor, dust, or fibers/flyings that will be present"
This text clearly shows that a piece of electrical equipment (like a DC power supply) rated and marked solely for C1D2 is not compatible in a C2D2 environment. Even though the equipment in this scenario is explosion proof in a vapor environment, since it does not contain separate markings for C2D2 and related groups, it is not rated for a C2 environment.
According to 2023 edition of NFPA 70 NEC 500.8.B.1 "Equipment shall be identified not only for the class of location but also for the explosive, combustible, or ignitible properties of the specific gas, vapor, dust, or fibers/flyings that will be present"
This text clearly shows that a piece of electrical equipment (like a DC power supply) rated and marked solely for C1D2 is not compatible in a C2D2 environment. Even though the equipment in this scenario is explosion proof in a vapor environment, since it does not contain separate markings for C2D2 and related groups, it is not rated for a C2 environment.