Is there a way to pass a Class I Div 1 connection through a standard enclosure?
I would like to place a small XP enclosure within a purged enclosure. The XP enclosure will provide power to the purge unit and a relay contractor to energize the purged enclosure when it is safe to do so.
How can I pass power through the Nema 4x enclosure to the XP Nema 7/9 enclosure inside?
I was looking at these Meyers hubs, but they are only rated to Class I Div 2.
We occasionally weld a female female conduit coupler into the wall of the panel for non-xp applications. I don't think that would be an option here (welding may reduce the integrity of the coupling).
I would like to place a small XP enclosure within a purged enclosure. The XP enclosure will provide power to the purge unit and a relay contractor to energize the purged enclosure when it is safe to do so.
How can I pass power through the Nema 4x enclosure to the XP Nema 7/9 enclosure inside?
I was looking at these Meyers hubs, but they are only rated to Class I Div 2.
We occasionally weld a female female conduit coupler into the wall of the panel for non-xp applications. I don't think that would be an option here (welding may reduce the integrity of the coupling).