Journeyman106
Member
- Location
- clarksville, tn
The situation we are having on-site here is that our standards require for our contractors to run TC cable from cable tray through conduit to the device being served. The question I have is this. In accordance with 501.15 (E)(1) it requires that multi-conductor cables to have their ends sealed when entering a device that is required to be explosion proof. However a little further down it tells you to refer to 501.15 (D) for multiconductor cables running through a conduit and in 501.15 (D)(2) it states that if the cable is capable of transmitting a gas or vapor then you must strip the outter insulation and pour around the individual conductors, but the exception to this states that if the cable passes through a seal-off within 18" of the device then the cable can be treated as a single conductor as long as the end of the cable is sealed.
Well the problem we have here is that most of our installations are complete but the seals have not been poured as of yet. I am trying to determine if I need to make the contractors go back and strip off the outer insulation of the cable and then pour the seals, or if they make something that will allow them to use the exception and seal the end of the cable?
Personally I do not see how gas can travel through the core of the cable since the cable originates in a non-classifed area and then goes to the device which is in a rated enclosure. I do understand the need to seal the conduit to keep the gas from entering into the disconnects through the conduit, but I am not sure how it will enter the cable, unless the gas gets into the disconnect and then travels through the cable back to the non-classified area.
This is all becoming very confusing and I need some assitance. My personal interpretation of the NEC is that the cable must be sealed where it enters the enclosure or the insulation must be stripped back at the seal-off and then poured. But this would mean alot of re-work and time and expense.
Any help would be greatly appreciated.
Well the problem we have here is that most of our installations are complete but the seals have not been poured as of yet. I am trying to determine if I need to make the contractors go back and strip off the outer insulation of the cable and then pour the seals, or if they make something that will allow them to use the exception and seal the end of the cable?
Personally I do not see how gas can travel through the core of the cable since the cable originates in a non-classifed area and then goes to the device which is in a rated enclosure. I do understand the need to seal the conduit to keep the gas from entering into the disconnects through the conduit, but I am not sure how it will enter the cable, unless the gas gets into the disconnect and then travels through the cable back to the non-classified area.
This is all becoming very confusing and I need some assitance. My personal interpretation of the NEC is that the cable must be sealed where it enters the enclosure or the insulation must be stripped back at the seal-off and then poured. But this would mean alot of re-work and time and expense.
Any help would be greatly appreciated.