I was wondering if I daisy chained two (2) transmitters via RS-485 on the hazardous side, to feed back to a barrier (isolator) on the safe side which will then feed back to a computer, and I still within bounds of intrinsic protection? Typical RS-485 driving voltage is around +12V if I remember correctly, but my concern was more with 2 processes coming into one line and being able to alter the signal on the cable depending on the process monitored. The voltage is still fairly low that I think I would still be within bounds. Capacitance of the cable is also extremely low.
This is all to receive a signal from the Magnetrol Contour transmitter to be used for Acoustic Volume Mapping of the inside of a bin.
Any feedback you may provide is greatly appreciated.
Thanks
Mike