We are designing in a IOT device into a Class I Div I Zone 1 IIc T4 location. Because it's a wireless device using small antennas, it is preferred to use a non-metalic cabinet as we have done for standard commercial installations.
The NEC requires metalic conduit as our 12V power is high enough in power to require protection. Highest voltage is 12VDC. We are designing our own I.S. barrier.
Question: Can we attach metal conduit to a suitably rated non-metallic cabinet? If so, what fittings are available? It isn't explosion proof, but we just need to seal out water as it is an outdoor installation. The box will have a vent as there is a barometer inside.