Somewhere i thought that i read you do not need a disconnect at a motor in a classified location becuase the disconnect would pose additional hazards. Did i see this or am i hallucinating again?
...example of an impractical...(a) if you only consider it "impractical"...
I'm just curious - I have read the FPN, but I cannot think of how the location of a disconnect (required to be in sight of the motor) introduces the hazards for some of the types of motor equipment listed.
Kent,
Some applications where the disconnect could be removed and there are provisions for lockouts on the starter would be a sewage pump station where there are 2-sides of the building (wet well & dry well) side. The building can be up to if not more that 3-stories deep. The MCC with starter is on the top floor, the pumps are located at the bottom of the pumping station with all process piping. The wet well typically has some lights with exhaust fans and level instruments all Class 1, Div 1 stuff where the local disconnects are small and still expensive. On the dry side there could be a potential for a flood and the equipment is usually 4X rated not always water proof, the pumps can be large and they are submersible type with a water tight cord connection to the motor. The cord is sleaved in conduit to the starter. Installing the disconnect at the lower level in Nema 4X could come in contact with water/sewage if flooded and start some sparks.
You are using the wrong word. The actual word is impracticable, with similar but yet distinguishably different meaning...
Those definitions didn't come from the Webster’s Collegiate Dictionary, 11th edition, which is the NFPA Manual of Style’s official dictionary. It finds impractical and impracticable virtually synonymous. It is the root dictionary at this site.I thought it was a typo. Silly me, I should have known there are no typos in the NEC. :wink:
Kent
Those definitions didn't come from the Webster?s Collegiate Dictionary, 11th edition, which is the NFPA Manual of Style?s official dictionary. It finds impractical and impracticable virtually synonymous. It is the root dictionary at this site.
I do believe I mentioned the CMP11 supporters intended impracticable to mean ?damn near impossible;? although you couldn?t prove it from any ROP/ROC.
However since lawyers are professional ?gnat strainers? and ?camel swallowers,? I wouldn?t put money that litigation would drive it in either direction since the CMP actually violated a couple of Manual of Style (MoS) rules.
To be frank, not once in the many NFPA Technical Committee (TC) meetings I attended did any TC consult with Webster?s Collegiate Dictionary, 11th edition. A few times the MoS was consulted ? such as determining practical is often an unenforceable term.