I need clarification on NEC 501.10 (B). I have a Class I Div 2 location containing various 4-20mA 24V sensors. The factory cables from these need to be joined in a box, and new shielded cables run in conduit.
According to the NEC Handbook "Any wiring method suitable for ordinary locations may be used for nonincendive field wiring" and 501.10 (B)(4) states that "Boxes and fittings shall not be required to be explosion proof except as required by 501.105(B)(1), 501.115(B)(1), and 501.150(B)(1). There are no arcing parts, transformers, etc in this location. I have to check if these circuits are considered "nonincendive" or not, but if they are, does this mean that a regular junction box (such as a bell box with screw cover) can be installed in this area?
My questions are these:
- Is the raceway required to be rigid, or could it be EMT?
- Is it acceptable to use bell boxes with a standard cord grip (to install the sensor cable into the bell box.)
Thanks-
According to the NEC Handbook "Any wiring method suitable for ordinary locations may be used for nonincendive field wiring" and 501.10 (B)(4) states that "Boxes and fittings shall not be required to be explosion proof except as required by 501.105(B)(1), 501.115(B)(1), and 501.150(B)(1). There are no arcing parts, transformers, etc in this location. I have to check if these circuits are considered "nonincendive" or not, but if they are, does this mean that a regular junction box (such as a bell box with screw cover) can be installed in this area?
My questions are these:
- Is the raceway required to be rigid, or could it be EMT?
- Is it acceptable to use bell boxes with a standard cord grip (to install the sensor cable into the bell box.)