We have an explosion proof box that we are putting in a class I div II location. The question is, would it be acceptable to place a standard A419 thermostat in the XP enclosure and run the cable through the enclosure to have the temp sensor in the class I div II room?
My interpretation of the code is that this is okay as long as there is a boundary seal and a process seal (501.17).
Another thing that I am curious about is how to determine if a cable is 'capable of transmitting gasses or vapors'. In the case that they are, the code states that they are to be sealed after the jacket and other coverings have been removed (501.15(E)(1)).
My interpretation of the code is that this is okay as long as there is a boundary seal and a process seal (501.17).
Another thing that I am curious about is how to determine if a cable is 'capable of transmitting gasses or vapors'. In the case that they are, the code states that they are to be sealed after the jacket and other coverings have been removed (501.15(E)(1)).