This question is about NEC Article 501.105(B).
The article provides guidance for instruments in Class I Division 2 area.
I have had many discussions with people of varying levels of experince and there seems to be widespread opinion regarding what kind of instrumentation is acceptable in a CID2 area and what kind of enclosures or additional protection is required.
The widespread opinion seam to stem from the Exceptions in 501.105(B)(1) versus the Exceptions in 501.105(B)(2)
(B)(1) clearly spells out a requirement for non-incendive, hermetically seals, oil immersed or listed devices. However (B)(1) applies only to Contacts
(B)(2) applies to Resistors and Similary Equipment and the exception for (B)(2) says that GP is permitted if it meets the T rating requirment and it has no contacts.
How do we apply this to general purpose instrumentation (generally 24VDC) such as flowmeters, DP meters, etc? How do people generally determine if any certain piece of instrumentation falls under the (B)(2) exceptions or not? Is this left up to the AHJ or is there a hard rule to go by. I have always applied the (B)(1) requirements to instrumentation, but with so many different opinions, I figured I would go get a few more :lol: .
The article provides guidance for instruments in Class I Division 2 area.
I have had many discussions with people of varying levels of experince and there seems to be widespread opinion regarding what kind of instrumentation is acceptable in a CID2 area and what kind of enclosures or additional protection is required.
The widespread opinion seam to stem from the Exceptions in 501.105(B)(1) versus the Exceptions in 501.105(B)(2)
(B)(1) clearly spells out a requirement for non-incendive, hermetically seals, oil immersed or listed devices. However (B)(1) applies only to Contacts
(B)(2) applies to Resistors and Similary Equipment and the exception for (B)(2) says that GP is permitted if it meets the T rating requirment and it has no contacts.
How do we apply this to general purpose instrumentation (generally 24VDC) such as flowmeters, DP meters, etc? How do people generally determine if any certain piece of instrumentation falls under the (B)(2) exceptions or not? Is this left up to the AHJ or is there a hard rule to go by. I have always applied the (B)(1) requirements to instrumentation, but with so many different opinions, I figured I would go get a few more :lol: .