You still appear to be applying conduit rules to a cable installation. They do apply ocassionally, but start with Section 501.15(E) for Division 2, cable installations. Section 501.15(E)(1) does cross reference to 501.15(B)(1) which further cross references to 501.15(A)(1)(1) and (A)(3).
Per your current description, you will need an explosionproof seal. You may as well assume that SOW is a "[m]ulticonductor cable with a gas/vaportight continuous sheath capable of transmitting gases or vapors through the cable core..." since no manufacturer will guarantee it won't "...transmit gases or vapors through the cable core."
That said, the SOW "... shall be sealed in a listed fitting in the Division 2 location after removing the jacket and any other coverings so that the sealing compound surrounds each individual insulated conductor in such a manner as to minimize the passage of gases and vapors.