One of the mechanical engineers where I work is specifying a piece of equipment that is (apparently) available as either Class I Group C or as Class I Group D. I've seen devices with a rated Group C and D, but this one is either one or the other. I don't know many more details, since I wasn't there for the conversation, but the advice he got from one of our electrical engineers was that Group C is "more hazardous", so he should get the equipment rated Class I Group C, and he would be covered in both.
I can understand this opinion. Looking at the descriptions, Groups B through D allow progressively larger safe gaps, so I guess you could interpret that a group B device could be installed in a group C location, if you wanted to. I just can't find anywhere in Article 500 that lets you install a group C device in a group D environment.
My feeling is that only a device listed for group D should be installed in a group D location. Can anyone offer any guidance, either to support my opinion or to convice me that I'm wrong, and this is ok?
Thanks,
Matt
I can understand this opinion. Looking at the descriptions, Groups B through D allow progressively larger safe gaps, so I guess you could interpret that a group B device could be installed in a group C location, if you wanted to. I just can't find anywhere in Article 500 that lets you install a group C device in a group D environment.
My feeling is that only a device listed for group D should be installed in a group D location. Can anyone offer any guidance, either to support my opinion or to convice me that I'm wrong, and this is ok?
Thanks,
Matt