Class I Zone I Multiwire branch Circiut

Status
Not open for further replies.

searlest

Member
A Multiwire branch Circiut is not permitted in a class I Zone I , Location unless all conductors of the circuit can be opened simultaneously

True or False

Code reference 505.22

I would answer True, however the answer key says false??

The onloy key word that is in the code exception that is not in the question is ungrounded!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The code reference should be 505.21 and it's exception.