I have reviewed table 110.20, in the past and have noticed that it shows an "X " in the windblown (outdoor) dust... column for NEMA 3 and 4, 4X and circulating (indoor) dust... column for NEMA 4, and 4X. Is your preference for NEMA 3 based on the FPN at the bottom of the table? I took the omission of NEMA 4 and 4x as an inadvertant error, which is curious, since the NEMA250 and UL50 standards both define 3, 4 and 4x the same with respect to dust tightness as well as the body table 110.20. I agree that the duct seal will not change that, but the objective here is to prevent dust migration through the conduit since there is no ignition source (arcing,sparking, or heat generating devices) inside the pullbox or LB and contains only nonincendive field wiring. So if duct seal is used at the conduit openings on a NEMA 3, 4, or 4X, transmission of dust from one location to another would not occur. The Form 7LB's have threaded bosses so wrenchtight connections prevent ingress of dust, but the gasket on the cover may still possibly allow some dust, but again the duct seal would prevent any migration.
Am I missing something???