Illinois
Member
- Location
- United States
A portable unit that we manufacture contains an electric motor (explosion proof Class I C&D, Class II F&G), about 24? of liquidtight conduit and a motor starter which is enclosed in a single gang box. Our customer adds a cord and plugs it into their power source which should be protected with a breaker.
We use only explosion proof motors rated Class I C&D, Class II F&G). I am trying to determine the requirement for the conduit and the enclosure which contains the motor starting switch.
To comply with Class II, Div1, although 502.10 (A) (2) leads me to believe Liquidtite conduit and fittings (Arlington in this case) are acceptable; however, 502.10 (A) (3) leads me to believe that I need both an explosion proof box and fitting for Class II, Div 1. I'm not sure which fittings we have to use, as the two seem to contradict each other. Any guidance?
For the enclosure/box, it seems pretty clear. I suppose we have to go with a box that is rated for Class 2 to be compliant for Class 2, Div 1. I take this to mean we have to use an explosion proof box. Do you agree, or would a Dust Tight box meet the Class 2, Div 1 requirement?
Any help is appreciated. If nothing else, perhaps you can point me in the right direction.
We use only explosion proof motors rated Class I C&D, Class II F&G). I am trying to determine the requirement for the conduit and the enclosure which contains the motor starting switch.
To comply with Class II, Div1, although 502.10 (A) (2) leads me to believe Liquidtite conduit and fittings (Arlington in this case) are acceptable; however, 502.10 (A) (3) leads me to believe that I need both an explosion proof box and fitting for Class II, Div 1. I'm not sure which fittings we have to use, as the two seem to contradict each other. Any guidance?
For the enclosure/box, it seems pretty clear. I suppose we have to go with a box that is rated for Class 2 to be compliant for Class 2, Div 1. I take this to mean we have to use an explosion proof box. Do you agree, or would a Dust Tight box meet the Class 2, Div 1 requirement?
Any help is appreciated. If nothing else, perhaps you can point me in the right direction.