For a Class II Div 2 (G) location, is a TEFC motor for pump or fan use with 40C ambient and class B or F wiring (SF 1.15) acceptable? The autoignition temperature is 300C.
502.8(B) would seem to indicate the enclosure was acceptable with a normal operating temp of 130C or 155C which is below the 165C limit in 500.8(C)(2).
502.8(B) would seem to indicate the enclosure was acceptable with a normal operating temp of 130C or 155C which is below the 165C limit in 500.8(C)(2).