Class1 Div 1 & Low voltage switches

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
Re: Class1 Div 1 & Low voltage switches

What do you mean for security? Do you mean a switch that will release a door or other mechanism by means of an electromagentic induction? Regardless of voltage, switches and the wiring to them will have to be listed for Class 1, Division 1 locations, and therefore be installed under the provisions of Article 501.
 

pbeci

Member
Location
Pennsylvania
Re: Class1 Div 1 & Low voltage switches

This is a normal security magnet switch you would find in a home alarm system. I have not seen the specifications on the device.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Class1 Div 1 & Low voltage switches

If it is a Class 1 Division 1 area, that switch cannot be used. See 501.6(A).
Also please do not double post your questions.
Don
 

charlie

Senior Member
Location
Indianapolis
Re: Class1 Div 1 & Low voltage switches

In some cases, that type switch may be used if it is listed for the purpose. You have to have an intrinsically safe system you are putting the switch on. I would think the security system would have a listing that would allow the use of the type switch that has a sealed glass bulb to enclose a reed switch. The whole system would have to be listed for the purpose and the installation instructions followed to the tee.
 

barrydmi

Member
Location
Washington
Re: Class1 Div 1 & Low voltage switches

The switch will not last long if in a sewage pit or well, because of corrosion. But installing a switching device in a Class1 div. 1 area is OK if it rated for it and routed through an intrinsically safe relay. Don't forget about seal offs of in conduit.
 