I have a location that is class1 div2. The switches are outside of the room near the door. Do they need to be xp? Is there a certain distance away that is still classified? Can you give me the section of code?
The primary concern, at the moment, is how the classification was determined in the first place. Without more information, I always raise an eyebrow when a room is only classified Class I, Division 2. If it wasn?t based on Articles 511 to 516 or a specific NFPA Standard, such as NFPA 820, it is much more likely to be unclassified depending on how the Class I materials are used or Division 1 depending on ventilation. If it did need to be Class I, very few rooms are adequately ventilated to drop from Division 1 to Division 2. Although there are a few other protection techniques in Section 500.7 that may permit treating it as a Division 2 location, they are rare applications.I have a location that is class1 div2. The switches are outside of the room near the door. Do they need to be xp? Is there a certain distance away that is still classified? Can you give me the section of code?
Very much like the OP you need to determine how the boundaries were/are fixed. Basically, "You gotta draw the line somewhere." As long as the wiring does not cross the boundary (the line), then what you described (what I underlined) is fine.I have a similar question. The code references the class 1 area in a commercial garage as being 18" above the "floor space." Does the wiring within finished walls fall under this designation? Basically, can the wiring concealed within the walls be installed below 18" as long as the receptacles and other devices are above 18"?
The primary concern, at the moment, is how the classification was determined in the first place. Without more information, I always raise an eyebrow when a room is only classified Class I, Division 2. If it wasn’t based on Articles 511 to 516 or a specific NFPA Standard, such as NFPA 820, it is much more likely to be unclassified depending on how the Class I materials are used or Division 1 depending on ventilation. If it did need to be Class I, very few rooms are adequately ventilated to drop from Division 1 to Division 2. Although there are a few other protection techniques in Section 500.7 that may permit treating it as a Division 2 location, they are rare applications.
Rating of the walls/doors is a bit less of a consideration; the primary concern for them is whether they are penetrated or not. Porosity is not generally a concern; a good coat of paint will solve that.
Find out what the basis of the classification is in the first place, THEN you can determine the boundaries.