Before you start thinking about any voltage, read and understand Section 504.10(A) and understand you cannot make the control drawing necessary for a compliant installation.
I used to think that the control drawings were a big deal too, but after a while I realized it's basically just the manufacturers instructions. Now it seems kind of curious that the NEC makes such a deal out of it when as a listed device you have to use it in accordance with the listing instructions anyway.It’s printed on the IS barrier as well as in the standard. There is nothing to 99% of these because it’s just PLC IO, it’s like loop sheets...a total waste of trees since we no longer typically have discrete field PIDs in most cases. I realize NEC makes a big deal out of this but it’s not.
Thanks for the infoIt’s printed on the IS barrier as well as in the standard. There is nothing to 99% of these because it’s just PLC IO, it’s like loop sheets...a total waste of trees since we no longer typically have discrete field PIDs in most cases. I realize NEC makes a big deal out of this but it’s not.
Simple devices don’t need Listing. There are two categories. One is it doesn’t generate more than 1.5 V, 100 mA, and 25 mW. This is for thermocouples. The other is a passive device that doesn’t consume over 1.3 W. At 24 V you are limited to 50 mA. That’s enough to drive a lot of NAMUR devices like level and flow sensors. It handles switches, some lights, and RTDs, The IS barrier takes care of the current and voltage limiting. More advanced devices are available with more complicated rules.