class1 division1 camera hook ups

Status
Not open for further replies.

pappasmurf

New member
so im running pipe for cameras that are explosion proof encased in a class1 division 1 building ,my question is their a flex able pipe I can use to connect to the cameras or do I have to run rigid directly into the cameras and if so do I have to use seals at those connections
 
so im running pipe for cameras that are explosion proof encased in a class1 division 1 building ,my question is their a flex able pipe I can use to connect to the cameras or do I have to run rigid directly into the cameras and if so do I have to use seals at those connections
They are called explosionproof flexible couplings. You will still have to seal the enclosure.
 