sgstrick
New User
- Location
- Murrells Inlet, SC USA
We are trying to confirm that NFPA 45 and NFPA 70 requirements for classifying a fuel testing lab room allow the designer to determine classification based on the hazard. NFPA Chap 5, sec 5.6.2 states they are unclassified with respect to Article 500 unless determined to cause a hazardous atmosphere. In a lab with a fume hood that is vented to the outdoors and has makeup air supplied, the hazard is controlled inside the hood, is there any other section of NFPA 70 or NFPA 45 that would require the entire lab room be classified as Class 1, Div 2?