I need some advice concerning the classification of an area (31'x19') where a E-cylinder of acetylene will be stored and piped for a chem lab testing method. I am tasked with installing a cabinet with 480-220 step down transformer and breaker panel within this room. This room will also contain several computer work stations.
It seems to me that this might be classified as Class 1, Div 2. or maybe not even calssified based on the fact that the acetylene will be very unlikely to be present in any concentration high enough to combust. The only thing that worries me is the accident condition. If the regulator becomes inoperable or the valve breaks due to impact, the volume culd quickly rise to a combustible mixture.
What are your thoughts about this?
It seems to me that this might be classified as Class 1, Div 2. or maybe not even calssified based on the fact that the acetylene will be very unlikely to be present in any concentration high enough to combust. The only thing that worries me is the accident condition. If the regulator becomes inoperable or the valve breaks due to impact, the volume culd quickly rise to a combustible mixture.