Checking an existing system and trying to decide whether to apply 250.66 or 250.122 to verify size of a grounding conductor?
Given, an industrial system, 1500 KVA pad mounted transformer, 480v, Y secondary, no neutral loads, no grounded conductor.This grounding conductor runs between two ground electrode systems, one ring at the transformer and one ring at the MCC. It is also connected to the grounding lug of the transformer and the MCC ground buss. Is it a grounding electrode conductor or an equipment grounding conductor? Here's the kicker...It is in the same conduit that encloses the transformer secondary conductors that feed the MCC main breaker (considered the service equipment in this case).
1. What do we call it?
2. if 250.122 applies to it's sizing and the transformer is not fused on the secondary, what do we use to size the conductor?
Appreciate any comments?
:?HE
Given, an industrial system, 1500 KVA pad mounted transformer, 480v, Y secondary, no neutral loads, no grounded conductor.This grounding conductor runs between two ground electrode systems, one ring at the transformer and one ring at the MCC. It is also connected to the grounding lug of the transformer and the MCC ground buss. Is it a grounding electrode conductor or an equipment grounding conductor? Here's the kicker...It is in the same conduit that encloses the transformer secondary conductors that feed the MCC main breaker (considered the service equipment in this case).