ealfordtcco
New member
what is the minimum distance required in front of a 480v appliance service panel?
I presume that the phrase ?service panel? is intended to mean a metal cover on one side of the appliance that you remove in order to gain access to the internals of the appliance (i.e., as opposed to a circuit breaker panel dedicated to service various appliance loads). To get an answer to your question, you first need to answer two questions: (1) Is it likely that a technician will be removing that panel to inspect or perform work on the internals of the appliance, without first turning off all power to the appliance? (2) When the technician works on the appliance, will the surface of the object behind him (or her) be connected to planet Earth? The most likely answer to both questions is ?Yes,? in which case your answer is ?42 inches.? But I will echo Ryan?s advice: look at NEC Article 110.26.Originally posted by ealfordtcco:What is the minimum distance required in front of a 480v appliance service panel?