"clearance code" for feeder junction box has spliced wires

Status
Not open for further replies.

mnka

New User
Location
85203
Occupation
electrical Contractor
what is NEC code states for "clearance area to be" for feeder junction box that has spliced wires in the box. Feeder are for 250 Amps 3-Phase
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
If you could physically make the installation and the splices you have enough space. 110.26(A) workspace is not required for pull and splice boxes.
 