M mnka New User Location 85203 Occupation electrical Contractor Oct 14, 2021 #1 what is NEC code states for "clearance area to be" for feeder junction box that has spliced wires in the box. Feeder are for 250 Amps 3-Phase
what is NEC code states for "clearance area to be" for feeder junction box that has spliced wires in the box. Feeder are for 250 Amps 3-Phase
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 14, 2021 #2 Are you thinking of a requirement in 110.26? If so please read the first section.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Oct 14, 2021 #3 If you could physically make the installation and the splices you have enough space. 110.26(A) workspace is not required for pull and splice boxes.
If you could physically make the installation and the splices you have enough space. 110.26(A) workspace is not required for pull and splice boxes.