Can we install 480V/3P/60A disconnect switch (serving motor) on wall, above 45KVA or 75kVA transformer? Does it meet code for required clearance? Or it needs to line up with transformer front? Thank you.
Correct. That may mean building out some support method to fasten it to instead of putting it directly on the wall behind the transformer.The face can be 6 inches behind the face of the transformer.
We build them out when the is limited wall space. Don't ask what those green conductors are for.
The one time I worked in an airport we had to put those jumpers in on all flex conduits, it was an FAA thing.
It is up for grabs. I tend to agree with you and my inspectors feel the same way.Am I the only one reading this as a maintenance disconnect that does not need to meet the 110.26 requirements?
On the other side of the coin, when the equipment fails I seen very few instances when the electrician won't check the disconnect for the presence of voltage.Am I the only one reading this as a maintenance disconnect that does not need to meet the 110.26 requirements?
110.26 has long been unclear as to exactly what it is supposed to cover. "likely to require examination, adjustment, servicing, or maintenance while energized" leaves the door wide open to interpretation.Am I the only one reading this as a maintenance disconnect that does not need to meet the 110.26 requirements?