Clearance from heater to conduit

Status
Not open for further replies.
Given the distance of the raceway from the heat source I don't see any issues. You could always adjust the conductor ampacity for the raise in air temperature but the 10'/10% rule probably wouldn't change a thing.
 
The only issue would be if the heat source causes the temperature of the conductors to rise above their rating of 90° C.
 
I'd say as long as it's not putting out air above 194 degrees farenheit things should be ok... :)


JAP>
 