Given the distance of the raceway from the heat source I don't see any issues. You could always adjust the conductor ampacity for the raise in air temperature but the 10'/10% rule probably wouldn't change a thing.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The only issue would be if the heat source causes the temperature of the conductors to rise above their rating of 90° C.
 

jap

Senior Member
Occupation
Electrician
I'd say as long as it's not putting out air above 194 degrees farenheit things should be ok... :)