Does anyone know if the NEC says anything about clearances of electrical conduits from water pipes?
 

BAHTAH

Senior Member
Location
United States
Re: Clearance from water pipes

300-8 States that raceways are designed for conductors and cables and prohibits raceways being used for nonelectrical components such as water lines. This does not prevent you from installing a water line with a conduit through a common raceway sleve etc. The water system is bonded to the electrical system.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Clearance from water pipes

As long as the piping is not in the 110.26 work space or equipment space there is no code rule about water pipes and electrical equipment.
Don
 