Clearance from water pipes

Status
Not open for further replies.

amp

New member
Does anyone know if the NEC says anything about clearances of electrical conduits from water pipes?
 
Re: Clearance from water pipes

300-8 States that raceways are designed for conductors and cables and prohibits raceways being used for nonelectrical components such as water lines. This does not prevent you from installing a water line with a conduit through a common raceway sleve etc. The water system is bonded to the electrical system.
 
Re: Clearance from water pipes

300-8 does not mention anything about clearance from water pipes. I do not know of any article that does.
 
Re: Clearance from water pipes

As long as the piping is not in the 110.26 work space or equipment space there is no code rule about water pipes and electrical equipment.
Don
 