Re: clearance in front of 480 V elevator controller
As Don is suggesting, what condition for Table 110.26(A)(1) would you consider for your room. If there are no exposed live parts or grounded parts on the other side of the equipment, then 3'. If there are exposed live parts on one side and grounded parts on the other, then 3.5'. Exposed live parts on both require 4'.