I don't know of any clearances just that it must be accessible. Probably an ahj call.
110.26 Requires access and working space to be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
So IMHO this section requires enough room to open the LB and remove or pull in new conductors.
Chris
If I can pull the wire and put the cover on, I consider that accessible. The ahj can not say otherwise, IMO.
So what operable and/or maintaineable parts does an LB contain?
So what operable and/or maintaineable parts does an LB contain?
110.26 Spaces About Electrical Equipment. Access and working space shall be provided and maintained about all electrical equipment to permit ready and safe operation and maintenance of such equipment.
We are to permit ready and safe operation of all electrical equipment. That statement would include the raceway on either end of the LB, much less the operable screws, removable cover, and removable conductors inside.
Equipment is equipment, and the parent section makes no conditions about how much maintenance or how much space is required. (A) begins being more specific and restrictive, but 110.26 itself is wide open.
The whole section is written horribly, it's always subject to interpretation as to how to apply it.
You understand that I am saying that the 30" x 36" does not apply, but an unspecified clearance does, right?
You understand that I am saying that the 30" x 36" does not apply, but an unspecified clearance does, right?