nvpowerdoc
Member
- Location
- Las Vegas, NV
Referring to Table 110.34(A), Minimum Depth of Clear Working Space at Electrical Equipment under "Condition II", what is the appropriate clearance for a medium voltage starter on an indoor enclosed 12kV system? Our AHJ inspector interprets this as 9001V - 25,000V, thus requires 6' clearance (based on equipment name plate rating of 12kV), though "Nominal Voltage to Ground" is 7200V.
The table specifically states "Nominal Voltage to Ground" in determining the voltage class.
Referencing 100 Definitions:
Voltage, Nominal. A nominal value assigned to a circuit or system for the purpose of conveniently designating its VOLTAGE CLASS (e.g., 120/240 volts, 480Y/277 volts, 600 volts).
and
Voltage to Ground. For grounded circuits, the voltage between the given conductor and that point or conductor of the circuit that is grounded; for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit.
Definition 1 places the starter in the 9001V-25kV class as a system, however definition 2 places the starter in the 2501V-9kV class.
The Engineer indicates 5' is required (based on phase to ground voltage). As the electrical contractor we can see both sides of the argument. What is the best way to interpret this table since the voltage ratings cross classes?
The table specifically states "Nominal Voltage to Ground" in determining the voltage class.
Referencing 100 Definitions:
Voltage, Nominal. A nominal value assigned to a circuit or system for the purpose of conveniently designating its VOLTAGE CLASS (e.g., 120/240 volts, 480Y/277 volts, 600 volts).
and
Voltage to Ground. For grounded circuits, the voltage between the given conductor and that point or conductor of the circuit that is grounded; for ungrounded circuits, the greatest voltage between the given conductor and any other conductor of the circuit.
Definition 1 places the starter in the 9001V-25kV class as a system, however definition 2 places the starter in the 2501V-9kV class.
The Engineer indicates 5' is required (based on phase to ground voltage). As the electrical contractor we can see both sides of the argument. What is the best way to interpret this table since the voltage ratings cross classes?