Clearances and Lighting panel

Status
Not open for further replies.

mltech

Senior Member
Location
Ft. Lauderdale
I have a very tight spot that I need to put a 3 phase 200 amp panel (15" wide) and a lighting control panel (15" wide) next to each other in a 46" wide area x 8' tall room.
To the left of the electrical panel will be a stacked washer/dryer (30"wide) and I only have 6" to spare before I need to mount the Electric and lighting panel in the 46" open wall space.
The Lighting control panel has a solid cover held on by screws with no cover doors that need to swing.
If I mount it next to my electrical panel it should not interfere with my working clearances of 30".
Right?
Thx for the input.
 
If I read correctly, the two panels add to 30" wide. You should be O.K. as long as neither of them has a depth 6" greater than the other. (110.26)(A)(3)
 