Re: clearances for service disconnects
110.26(B) Clear Spaces. ?Working space required by this section shall not be used for storage.?
It is arguable as to whether a roll-away table would constitute ?storage,? but I would try to get the table moved elsewhere. By the way, I am guessing you did not mean ?service? disconnect, but rather a disconnect for a specific component. That might not change the code interpretation, but it might. If there is no reason to ever expect that the disconnect would require ?examination, adjustment, servicing, or maintenance while energized,? then the working clearances would not apply.