G GerryB Senior Member Location woodbridge, ct. USA May 18, 2017 #1 Does 110.26(E)(1)a include transformers, disconnects or j-boxes? Specifically this case there is water piping above the transformer, over 6 feet but below the structural steel.
Does 110.26(E)(1)a include transformers, disconnects or j-boxes? Specifically this case there is water piping above the transformer, over 6 feet but below the structural steel.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer May 18, 2017 #2 No. That article lists four items to which it applies. It applies to nothing else.
G GerryB Senior Member Location woodbridge, ct. USA May 18, 2017 #3 charlie b said: No. That article lists four items to which it applies. It applies to nothing else. Click to expand... Thank you, that is what I thought.
charlie b said: No. That article lists four items to which it applies. It applies to nothing else. Click to expand... Thank you, that is what I thought.