Re: Clearence Of 480v Disconnect
36" is correct of condition 1 (Exposed live parts on one side of the working space and no live or grounded parts on the other side of the working space, or exposed live parts on both sides of the working space that are effectively guarded by insulating materials.)
Condition 2 requires 42" for nominal voltages to ground of 151-600 (Exposed live parts on one side of the working space and grounded parts on the other side of the working space. Concrete, brick, or tile walls shall be considered as grounded.)
Condition 3 requires 48" for nominal voltages to ground of 151-600 (Exposed live parts on both sides of the working space.)
Also take a look at 110.26 (A) Working Space. Working space for equipment operating at 600 volts, nominal, or less to ground and likely to require examination, adjustment, servicing, or maintenance while energized shall comply with the dimensions of 110.26(A)(1),(A)(2), and (A)(3) or as required or permitted elsewhere in this code.
Chris