If the power company gives me clearing time on primary of a 750 kva transformer, how does that apply to secondary? He is going to give me fault current on secondary
If the power company gives me clearing time on primary of a 750 kva transformer, how does that apply to secondary? He is going to give me fault current on secondary
That is an odd thing for the utility to give you.If the power company gives me clearing time on primary of a 750 kva transformer
We need to update our arc flash labels on all of our equipment and this is the starting point by contacting the utility to get available fault current. None of it has had a study and the old labels were just a wild guess. Our new procedure has a matrix for ppe selection with no analysis done and it has short circuit current available and clearing time as part of ppe and arc flash boundary. Mostly for loto testing and trouble shooting since we can turn it off and don’t work energized. But we have to fill out jsa and wear proper PPE to comply with our safety department with no arc flash analysis
Thank you all for your replies. I am just a E&I tech and after they rolled out our new procedures was voluntold to contact utility to ask for fault current. As you know the company is supposed to do an analysis and provide labels for 70e. I know just enough to know that a Qualified Engineer needs to do those calculations. The Utility guy is coming Monday to look at facility and get a list of transformers to their engineering to get some info. This station is our biggest. Most the others are just one drop with 400 or 200 amp 480 disconnect. With what you guys replied, that gives me what to ask for from utility.
I don't think you quite know what to do for the incident energy. You most likely get the infinite bus secondary current but if you do get the available fault current, then you need to determine the trip time of the protective device upstream from a TCC. Do you have all those? You will have to calculate the fault current at each piece of equipment where you need to determine the clearing time to use the table method. Do you know how to do that? Also, what do you do if there is a protective device that is overdutied? Are you checking for that?
This is not an area to be on a learning curve and make a mistake. This is PPE to protect a fellow employee from serious injury or even a fatality. You should let a qualified engineer experienced in these studies do the work.