Hey All!
My client bought 115' of URD cable for a run from the meter to a new garage they are building. Problem is by code we are required to install an outside disconnect which means we need to run 3 conductors and a ground wire. URD is 2 conductors and a "Neutral".
Client can't return the cable, and would like to use it if possible. I want to recommend that we use the URD cable and run an additional 4/0 USE-2 wire along side the cable. The 2/0 on the cable can be used as the ground, and the additional 4/0 can be used as neutral. Before recommending this to the client I wanted to make sure my thought process was right.
Thanks!
My client bought 115' of URD cable for a run from the meter to a new garage they are building. Problem is by code we are required to install an outside disconnect which means we need to run 3 conductors and a ground wire. URD is 2 conductors and a "Neutral".
Client can't return the cable, and would like to use it if possible. I want to recommend that we use the URD cable and run an additional 4/0 USE-2 wire along side the cable. The 2/0 on the cable can be used as the ground, and the additional 4/0 can be used as neutral. Before recommending this to the client I wanted to make sure my thought process was right.