I've had a potential client approach me with a somewhat unusual request. They have a project that requires a new service. Their original contractor pulled permits, took the deposit, and disappeared. Now they are several months behind, and don't want to/can't wait on the 6-month+ lead time for the spec'd panels. They've asked me to come up with an alternative using readily/quickly available equipment. This is a rural jurisdiction that will accept a one-line, panel schedule, load calcs, etc from a licensed EC, so I don't have to involve an EE unless things get complicated, although I may just for CYA reasons.
The original service was designed to be 600A single-phase with a 600A fusible disconnect feeding two MLO 600A 3R panel boards in series, with the first being feed-thru. (20) 50A circuits feeding power pedestals, (2) 125A circuits and (1) 200A circuit for sub panels, and a handful of 20A convenience receptacle circuits. Obviously the best solution is to wait on the spec'd equipment, and I'm going to push that, but it may not be an option.
My first thought was this:
600A fusible disconnect with parallel 300 MCM Cu fed through a trough. (6) sets of taps with 5-port Polaris connectors, feeding (2) 125A fusible disconnects, (1) 200A fusible disconnect, and (3) 200A main-breaker 3R panel boards. All this is outdoors and built on a rack. Obviously with an appropriately sized trough and tap conductors.
It works on paper, but is it compliant? The feeders don't terminate anywhere except the last set of Polaris connectors, is this a problem? I'm familiar with tap rules, but we're mainly residential and light commercial so we aren't using them often.
Its going to be large, kinda ugly, and probably cost just as much or more than doing it the "right" way by the time it's all said and done. I don't like using all those Polaris connectors like that, but I'm not finding gutter taps that are made for a parallel feed.
The original service was designed to be 600A single-phase with a 600A fusible disconnect feeding two MLO 600A 3R panel boards in series, with the first being feed-thru. (20) 50A circuits feeding power pedestals, (2) 125A circuits and (1) 200A circuit for sub panels, and a handful of 20A convenience receptacle circuits. Obviously the best solution is to wait on the spec'd equipment, and I'm going to push that, but it may not be an option.
My first thought was this:
600A fusible disconnect with parallel 300 MCM Cu fed through a trough. (6) sets of taps with 5-port Polaris connectors, feeding (2) 125A fusible disconnects, (1) 200A fusible disconnect, and (3) 200A main-breaker 3R panel boards. All this is outdoors and built on a rack. Obviously with an appropriately sized trough and tap conductors.
It works on paper, but is it compliant? The feeders don't terminate anywhere except the last set of Polaris connectors, is this a problem? I'm familiar with tap rules, but we're mainly residential and light commercial so we aren't using them often.
Its going to be large, kinda ugly, and probably cost just as much or more than doing it the "right" way by the time it's all said and done. I don't like using all those Polaris connectors like that, but I'm not finding gutter taps that are made for a parallel feed.