I would have no qualms also puting the HCS-40P on a 40A circuit as well. If anyone asks, show them the specs for the HCS-40. The units are identical except one comes with a plug and cord instead of a whip.
I wonder if this should be in the code forum? Sorry I started it in here. Here is what just went to Clipper Creek:
This email has two points/questions we would like addressed please, question 3 is an alternate for question 2. The primary issue is the client having to pay for a larger circuit than is necessary solely because they opted for a cord connection.
(1)
The HCS-40, 30A, 240V Charging, 25? Cord charges at 30 amps and requires a 40 amp breaker:
"Service Entrance: 208V to 240V, 60Hz ? 40 Amp Circuit (30A continuous for charging), single phase, 2-wire, with ground (L1, L2, and Ground)? Conduit and pigtail supplied"
If a client were to tell us they were purchasing a HCS-40 we would tell them a 40amp circuit is necessary.
The HCS-40P, 30A, 240V Charging, 25? Cord, NEMA 14-50 Plug is the same exact unit but with a 50 amp rated cord and plug. Your specifications states a 50 amp circuit:
?Service Entrance: 208V to 240V, 60Hz ? 50 Amp Circuit (30A continuous for charging), single phase, 2-wire, with ground (L1, L2, and Ground)? NEMA 14-50 plug in connection?
Both units at 30amp continuous with two different branch circuit ratings.
If they have an existing 40amp circuit to the garage, it is of no value with the corded unit.
We must now tell the client they have to pay more for the installation of the corded unit merely because your instructions mandate larger wires.
One ?might? reason with an inspector, but we would prefer that the installation instructions specifically state that the branch circuit may be rated at 40 amps because section 110.3(B) specifically states:
?(B) Installation and Use. Listed or labeled equipment
shall be
installed and used in accordance with any instruc-
tions included in the listing or labeling.?
(Underline/bold/italics by me)
So, when the instructions provided with the unit states 50 amps, a rule oriented inspector will mandate this as the UL interprets labeling to include the documentation provided with the unit and your unit is UL listed/labeled. It does not matter what any other code may state because the manufacturer has stipulated a 50amp circuit.
Our expectation is not to receive a discourse on why Clipper Creek should mandate a 50 amp circuit, though you may opt to do so, but rather a letter of modification we may insert into the documentation and a modification made to future documentation that stipulates a minimum 40amp branch circuit for both units.
(2)
Do the HCS-40 and the HCS-40P both have internal protection that opens all ungrounded conductors if an amperage draw exceeding 125% of the unit?s rating occurs?
(3)
Or, may the unit draw any amperage with no possibility of a fire?
Thank you in advance for any help you may provide.