Hello there :

unforetally i kinda in bind with this website here i try to find a photo what MHS* did have a photo of the clothes cloest with the demison how far the lumiaire located

this part is in 410 ??

the reason why because i have new NEC code book printed in french and seems i found a blunder [ error ] so i will like to heard your feed back on this matter

thanks you for reading this

Merci , Marc

P.S. * MHS = Mike Holt Site
 
Last edited:
Unfortunately I'm kinda in a bind with this website. I'm trying to find a photo that MHS* had, a photo of the clothes closet with the dimensions showing how far the luminaire can be located from the nearest point of storage space.
I'm not sure where the photo is you're speaking of, but the diagram in the NEC dictating exactly where the boundaries of the storage space are is Figure 410.8.

Once that's ascertained, the distance we can install luminaires beyond that space is given in 410.8(D).

The reason why because i have new NEC code book printed in french and seems i found a blunder [ error ] so i will like to heard your feed back on this matter.
What is the error you've noticed?
 