can somebody help me out on how a close-transition wye-delta starter works (reference sites)?
we have a new customer which employs this kind of starter on his 150KW, 440V, 249 FLA compressor motor...he was not able to use the motor because the utility's 225 KVA xf bank fuses all blew a few secs after the motor was started...we monitored the current in another attempt and the sequence were: start-on at wye the load was 530A...10 secs later the delta contactors closed and the load dropped to 130A...another second later the load shot up to 1,270A (almost a locked rotor condition)..this condiion was sustained for 1 sec before the xf bank fuses blew again...the starter supplier is still at a loss of what transpired....what could have caused the problem? i believe it is more likely to be a fault on the starter...
thanks for sharing your thoughts....
we have a new customer which employs this kind of starter on his 150KW, 440V, 249 FLA compressor motor...he was not able to use the motor because the utility's 225 KVA xf bank fuses all blew a few secs after the motor was started...we monitored the current in another attempt and the sequence were: start-on at wye the load was 530A...10 secs later the delta contactors closed and the load dropped to 130A...another second later the load shot up to 1,270A (almost a locked rotor condition)..this condiion was sustained for 1 sec before the xf bank fuses blew again...the starter supplier is still at a loss of what transpired....what could have caused the problem? i believe it is more likely to be a fault on the starter...